About a month ago I was asking a question about 'Relay Contact Ratings'.
I wrote:
" If you look at a typical Allen-Bradley output Module (in this example 1746-0W8) and read the specifications you will see this;
MAKE: BREAK:
120VAC 15A 1.5A
->] [<- <-] [->
What are they trying to explain/communicate here? "
Your Replay was:
The ratings you mentioned are the 120VAC ratings. The contacts have different make/break ratings. In other words when the output is energized and the contacts close or 'make,' the contact can handle an inrush of 15A. When you go to turn off the output and the contact has to open or 'break,' the contact should have no more than 1.5A of current accross it. Any time you break a circuit, you get arcing. Different contacts can handle greater or lesser amounts depending on their design.
So .... That brings me to my next question ........
When the Contacts 'Break' the current across then could "pit" the surface of the contacts - decreasing the life expectancy of the relay contacts.
Isn't there something called a "Snubber" circuit across the output terminals to decrease the arcing that occurs? especially when having an inductor (ie: coil)
connected to the output. maybe some type of circuit to dampen the sudden increased, rush of current?
Thanks for considering my question.
klm