Inserting JMP online with ControlLogix 
Hi I was just wondering is it possible to put a JMP and Label instruction in On-Line on the ControlLogix. If I put the JMP intruction in, then the PLC will not recognize the label to jump to until I insert this. This I take it will fault the PLC. Is there any way around this?
 
New Post 3/3/2009 4:15 PM
  AutomationNC
72 posts
Helper


Re: Inserting JMP online with ControlLogix 
I believe a Major Fault will occur if there is no associated label to jump to. Put the LBL rung in first, then assemble your edits. The CLX will run happily with a LBL and no JMP. Then put the JMP instruction in. Take care with your LBL rung placement. If you need to move it using online edits I believe the controller faults (Duplicate LBLs). Also important - make sure you assemble between the two edits. Assembling together will probably cause a fault.
 
Previous Previous
 
Next Next
  Forum  PLC Programming  Allen Bradley  Inserting JMP online with ControlLogix
  
 

 

  
Like this Site?

Check out our PLC Training Facebook site and "like" us!

Click Here!

  
Squidoo

Checkout our new Squidoo lens!  We have posted an interview with Russell White on PLC training.

To see it Click Here!

Let't wake up Squidoo and let them know we are here!

  
Terms Of Use  |  Privacy Statement
Home  |  Subscriptions  |  Training Videos  |  PLC Training  |  Articles  |  PLC Training Forum  |  Contact  |  About Us
Copyright © 2008 - 2011 by Automation Technologies, Inc. - All Rights Reserved